1MW power is to be delivered from a power station to town 10 km away. One uses a pair of Cu wires of radius 0.5 cm for this purpose. Calculate the fraction of ohmic losses to power transmitted if
(i) power is transmitted at 220 V. Comment on the feasibility of doing this.
(ii) a step-up transformer is used to boost the voltage to 11000 V, power transmitted, then a step-down transformer is used to bring voltage to 220 V.
(ρcu=1.7×108 SI unit )
PhysicsAlternating Current
Solution:
2403 Upvotes Verified Answer
(i) According to the question, the town is 10 km away, length of pair of copper wires used,
L=20 km=20000 m
Resistance of Cu wires,
R=ρl A=ρlπ(r)2
As given that, ρCu=1.7×108;r=0.5 cm
=1.7×108×200003.14(0.5×102)2=4Ω
As given that, P=1MW=106 watt
So, I at 220 V,P=VI=106 W,
I=106220=0.45×104 A
Power loss
P=RI2=4×(0.45)2×108 W=8.26×107 W
Power loss in heating
=82.6MW as 82.6MW>106 W
So, this method cannot be used for transmission.
(ii) When power P=106 W is transmitted at 11000 V.
VI=106 W=11000I
Current drawn, I=11.1×102
RCu=4Ω
(P) Power loss =RI2=11.21×4×104
P=3.3×104 watt
So, Fraction of power loss =3.3×104106=0.033
Hence, ( Power loss )=3.3%